PostPosted: 11:39 - 19 May 2013    Post subject: Boiler primary flow ploblem Reply with quote

Hi,
Before I begin I'll point out at no point would I touch the gas side of my boiler. I maybe soft but I'm not daft Very Happy
Started having a problem recently were my Halstead boiler (piece of crap I know) locks out as it hasn't detected a flow. Looking inside I noticed that the plunger which pushes the primary flow microswitch is very sluggish. When water has been run and the plunger is extended it retracts very slowly when the hot water tap has been turned off. Sometimes it doesn't retract fully so the microswitch contact isn't broken.


I replaced both the diagrpphams, gland nuts and microswitches over 3 years ago and have had no problems since (besides the secondary heat exchanger which regularly furs up.)

Prior to this problem the pump made a very loud noise one night as if it were stuck or struggling. Not sure if this maybe related.

Any suggestions as to what the problem may be?
 Back to top
View user's profile Send private message You must be logged in to rate posts

crazymotorbik...
Nearly there...



Joined: 05 Mar 2006
Karma :

PostPosted: 11:53 - 19 May 2013    Post subject: Reply with quote

Sorry wrong section.. darn my fat fingers...


please can someone move this
 Back to top
View user's profile Send private message You must be logged in to rate posts

calyx
World Chat Champion



Joined: 11 Dec 2008
Karma :

PostPosted: 19:43 - 19 May 2013    Post subject: Reply with quote

I would start with bleeding the pump.
Actually I am lying. I would start with buying a Viessmann boiler.
And I agree with moving the thread idea Laughing
____________________
Boris - London
 Back to top
View user's profile Send private message You must be logged in to rate posts

L4Isoside
World Chat Champion



Joined: 08 Mar 2010
Karma :

PostPosted: 20:41 - 19 May 2013    Post subject: Reply with quote

So is the problem with heating or hot water? You say primary flow but then mention what sounds like a diverter valve with a plunger pushing a microswitch for domestic hot water.. ?

If it is the diverter valve for the domestic water, providing its the type with a diaphragm pushing out a pin making a microswitch, it could well be that it's self which is causing a problem. May be struggling to push in/ out, meaning the boiler may not see a demand for hot water and possibly mean that it's sends it heat around the plate heat exchanger rather than the central heating flow?

Just an educated guess I do not know the boiler exactly.
 Back to top
View user's profile Send private message You must be logged in to rate posts
Old Thread Alert!

The last post was made 10 years, 316 days ago. Instead of replying here, would creating a new thread be more useful?
  Display posts from previous:   
This page may contain affiliate links, which means we may earn a small commission if a visitor clicks through and makes a purchase. By clicking on an affiliate link, you accept that third-party cookies will be set.

Post new topic   Reply to topic    Bike Chat Forums Index -> The Geek Zone All times are GMT + 1 Hour
Page 1 of 1

 
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You cannot download files in this forum

Read the Terms of Use! - Powered by phpBB © phpBB Group
 

Debug Mode: ON - Server: birks (www) - Page Generation Time: 0.07 Sec - Server Load: 0.24 - MySQL Queries: 18 - Page Size: 41 Kb