PostPosted: 12:23 - 23 Dec 2014    Post subject: Power to the shed Reply with quote

In a couple of weeks we get our garden project underway. It involves a lot of earthworks, a patio, driveway etc. There will also be a hard-standing area for a shed. The shed is on order - a decent 10'x6' apex-roof jobbie.

We currently have a weatherproof external double power socket on the back wall of the house (see diag). I assume this is a spur off of a socket on the mains running inside the house.

How best to get power to the shed? It will only need to be for lighting (probably LED) and a couple of 13A sockets. The shed will mostly be storage, maybe a little workshop bench. It will never be used for heavy-duty stuff (I can do anything like this in the garage, should I ever need to).

I thought about running some armoured cable whilst the ground was dug for the paving area, but where to run it to? To the existing waterproof sockets (and terminate with a 13A plug)? Or to the nearest wall of the house, where there are numerous sockets inside (the nearest bit of the house is a kitchen). Can I take a spur off of an existing internal socket, through the wall, with an appropriately protected junction box outside, or something?

I want to avoid trailing/tacked cable runs as much as possible, but would be OK with a short amount down into the ground from socket height.

Also, could I create a 'lighting circuit' and 'power circuit' in the shed, from one feed, or should I just install sockets and use plugged lighting?

Additional info: the consumer unit is in the centre of the house and does have one spare location. I could feasibly run cable from here, through the integral garage and out through an external wall, but this would be more disruptive and more cable-traily.
____________________
Yamaha XJ600 | Yamaha YZF600R Thundercat | KTM 990 SMT | BMW F900XR TE
 Back to top
View user's profile Send private message You must be logged in to rate posts

weasley
World Chat Champion



Joined: 16 Oct 2010
Karma :

PostPosted: 13:28 - 23 Dec 2014    Post subject: Reply with quote

OK, a bit more reading suggests this is one of those things that needs doing properly. It seems a spur off the mains is allowed, but not by me (unless I get the design, plans and installation checked, tested and verified). Think I might get someone in to look at it (no offence to the BCF).
____________________
Yamaha XJ600 | Yamaha YZF600R Thundercat | KTM 990 SMT | BMW F900XR TE
 Back to top
View user's profile Send private message You must be logged in to rate posts

Ribenapigeon
Super Spammer



Joined: 20 Feb 2012
Karma :

PostPosted: 13:38 - 23 Dec 2014    Post subject: Reply with quote

I would run the cable the shortest route possible. Armoured cable is pricey and what you would save would probably pay for a sparky to sign off the job. I would run a cable from the spare consumer box to a second box in the shed the make a lighting circuit and socket circuit in the shed. That way if a power tool trips the RCD you wont also have the lights go out. I'm not sure if this is legal though or if the main armoured supply would have to be rcd protected as well which would sort of defeat the point of a second consumer box.
 Back to top
View user's profile Send private message You must be logged in to rate posts

bugeye_bob
World Chat Champion



Joined: 05 Sep 2013
Karma :

PostPosted: 13:52 - 23 Dec 2014    Post subject: Reply with quote

How far away is your mains board, ideally see if you can run it all the way back.
 Back to top
View user's profile Send private message You must be logged in to rate posts

robs321
Could Be A Chat Bot



Joined: 24 Feb 2010
Karma :

PostPosted: 16:12 - 23 Dec 2014    Post subject: Reply with quote

The cheapest way to do it, is to make sure that the outside socket (presuming its RCD protected) is wired into a switched fuse spur. Then take a 2.5mm 3 core SWA off that (use external glands), if the run is not miles?. Run this to your sockets and another switched fuse spur. Use the spur in the shed with a 3 or 5 amp fuse and take your lights from that.
You will never over load the circuit because everything is wired into the switched fuse spur (13amp) indoors, that the original socket is joined too!
If there is a fault at any time, it can all be isolated from the house via the switched fuse spur.
 Back to top
View user's profile Send private message Send e-mail You must be logged in to rate posts

Howling TerrorOutOfOffice
Super Spammer



Joined: 05 Dec 2008
Karma :

PostPosted: 16:54 - 23 Dec 2014    Post subject: Reply with quote

My one tip.
Get a bigger shed. Girth is where it's at with sheds.
____________________
Diabolical homemade music Bandcamp and Soundcloud
Singer songwriter, Artist and allround good bloke Listen to Andrew Susan Johnston here
The Harry Turner Project
 Back to top
View user's profile Send private message Visit poster's website You must be logged in to rate posts

stinkwheel
Bovine Proctologist



Joined: 12 Jul 2004
Karma :

PostPosted: 16:57 - 23 Dec 2014    Post subject: Reply with quote

It would be better to have a secondary consumer unit in your shed with a lighting and ring RCD. Most of the things you'd be plugging in in a shed wsould warrant that degree of cover.

Either fed from a spare, non-RCD slot in your consumer unit or by adding a new tail from the meter.

Meantime. Conduit is cheap. Lay your conduit from house to shed with a rope through it when you're doing the groundworks and you can then decide at your leisure how you're going to do the electrical install.
____________________
“Rule one: Always stick around for one more drink. That's when things happen. That's when you find out everything you want to know.
I did the 2010 Round Britain Rally on my 350 Bullet. 89 landmarks, 3 months, 9,500 miles.
 Back to top
View user's profile Send private message You must be logged in to rate posts

weasley
World Chat Champion



Joined: 16 Oct 2010
Karma :

PostPosted: 17:26 - 23 Dec 2014    Post subject: Reply with quote

Thanks all. So conduit over armoured cable? I like the idea, as it is something I can do easily and then just get a spark in for one day to do the sparky bits.

Conduit; is that ribbed bendy pipe stuff a good idea, or are we talking PVC pipework?
____________________
Yamaha XJ600 | Yamaha YZF600R Thundercat | KTM 990 SMT | BMW F900XR TE
 Back to top
View user's profile Send private message You must be logged in to rate posts

ws4936
World Chat Champion



Joined: 10 Sep 2009
Karma :

PostPosted: 17:59 - 23 Dec 2014    Post subject: Reply with quote

I've personally done this...twice. I have a garage read: plastic shed on the front driveway and a shed out the back. Both are plastic keter big f'off jobbies, and both have armorured cable going to a junction box, then twin and earth going from the junction box to a consumer unit with light and electric circuits run from that.
Armoured cale isn't that expensive(ok it is compared to normal cable - but not in the grand scheme of things) and if anyone that you meet and haven't instructed not to use a spade in your yard, uses a spade in your yard, they will go throu conduit and cable. Do it right, do it once.

/pieceofmind


https://i.share.pho.to/f52c75a3_o.jpeg
____________________
If everything seems under control, you're just not going fast enough.
 Back to top
View user's profile Send private message You must be logged in to rate posts

kawakid
World Chat Champion



Joined: 15 Mar 2005
Karma :

PostPosted: 18:27 - 23 Dec 2014    Post subject: Reply with quote

I had a similar issue.

I ended up using armoured cabling and putting a consumer unit with 2 rings in it.

The laws have changed since I put it in, as you were allowed to do it by yourself back then.

Saying that, I doubt it would stop me now, though I do know 2 sparks, who I would just get to sign it off anyway.
____________________
I've a twin and a 4.
 Back to top
View user's profile Send private message You must be logged in to rate posts

drzsta
World Chat Champion



Joined: 20 Apr 2009
Karma :

PostPosted: 18:29 - 23 Dec 2014    Post subject: Reply with quote

Get an electrician to do it. Seeing those inspection elbows on that pvc conduit Sick looks naff.
 Back to top
View user's profile Send private message You must be logged in to rate posts

weasley
World Chat Champion



Joined: 16 Oct 2010
Karma :

PostPosted: 18:31 - 23 Dec 2014    Post subject: Reply with quote

Food for thought.

If I got some armoured cable and ran some under the paving area, leaving a decent length free at either end, will this satisfy a competent sparky, or would they need to physically see it laid in order to complete the job and certify it?

I am reluctant to get someone out to lay cable, then have to come back to do the shed work.
____________________
Yamaha XJ600 | Yamaha YZF600R Thundercat | KTM 990 SMT | BMW F900XR TE
 Back to top
View user's profile Send private message You must be logged in to rate posts

stinkwheel
Bovine Proctologist



Joined: 12 Jul 2004
Karma :

PostPosted: 18:36 - 23 Dec 2014    Post subject: Reply with quote

If you've put the conduit in, you can pull the cable through later and make it the correct length to go to both ends in one run.

I suggested it because I presumed you were already on the groundwork phase but still undecided on how you were running the wires and where to.

Having a nice plastic tube you can just run the cable up through makes the install a piece of piss if and when you decide to do it.

There's two sorts of conduit. One is that simple plastic spiral stuff. If you were using that, I'd use armoured cable through it.

Then there is armoured, waterproof stuff like kopex. Effectively the armour you'd find outside the armoured cable. If it's terminated correctly, you should be able to use standard mains cable inside it. IP67 rated, nothing is getting through that sucker but it's expensive.

If I was doing the job. I'd bung in some cheap, spiral plastic conduit for now while I have the hole in the ground (you can have it coming up through the concrete shed base). I'd pull my armoured cable through once I'd decided exactly where and how I was doing it. You could do a second piece to drag a water pipe through in case you ever decide to put a tap in.

Same thing as I did when I had a new base put down for an oil tank. I had the conduit put in at the same time then pulled the pipework through when the tank was actually fitted.
____________________
“Rule one: Always stick around for one more drink. That's when things happen. That's when you find out everything you want to know.
I did the 2010 Round Britain Rally on my 350 Bullet. 89 landmarks, 3 months, 9,500 miles.
 Back to top
View user's profile Send private message You must be logged in to rate posts

drzsta
World Chat Champion



Joined: 20 Apr 2009
Karma :

PostPosted: 18:41 - 23 Dec 2014    Post subject: Reply with quote

Lay it yourself, 450mm would probably suffice under paving out to 500mm/600mm if under lawn. No actual definitive depth in the regs - just that it should be at an adequate depth to prevent from being damaged.
 Back to top
View user's profile Send private message You must be logged in to rate posts

Chuffin Nora
World Chat Champion



Joined: 02 Sep 2013
Karma :

PostPosted: 18:59 - 23 Dec 2014    Post subject: Reply with quote

Erm.

Might one enquire as for what purpose this shed is intended?

And, on a not unrelated point, who owns the house/wears the trousers?

Because . . .
____________________
There's a fine line between integrity
 Back to top
View user's profile Send private message You must be logged in to rate posts

Furrybiker
Trackday Trickster



Joined: 07 Mar 2010
Karma :

PostPosted: 21:43 - 23 Dec 2014    Post subject: Reply with quote

Hate to hijack this but can I just ask a quick question?

I have a shed that I would like to power from the supply to the garage. It is only for a 150 watt security lamp and is about 15 metres from the garage.

Could I not just run an armoured cable from the RCD protected supply in the garage to the shed?

Or does this put me in breach of the regs?
 Back to top
View user's profile Send private message You must be logged in to rate posts

janner_10
World Chat Champion



Joined: 26 Sep 2011
Karma :

PostPosted: 22:23 - 23 Dec 2014    Post subject: Reply with quote

drzsta wrote:
Get an electrician to do it. Seeing those inspection elbows on that pvc conduit Sick looks naff.


Thats the way it is now - gone are the days of doing old school in pyro or conduit.

Most sparks would lash it in this way. But price > looks nowadays.
____________________
Yamaha FZS600 (Now gone to heaven) > CBR600F4i (SOLD) > '99 YZF-R1
 Back to top
View user's profile Send private message Send e-mail You must be logged in to rate posts

janner_10
World Chat Champion



Joined: 26 Sep 2011
Karma :

PostPosted: 22:25 - 23 Dec 2014    Post subject: Reply with quote

Furrybiker wrote:
Hate to hijack this but can I just ask a quick question?

I have a shed that I would like to power from the supply to the garage. It is only for a 150 watt security lamp and is about 15 metres from the garage.

Could I not just run an armoured cable from the RCD protected supply in the garage to the shed?

Or does this put me in breach of the regs?


Yes no harm. It was there when you moved in wasn't it?
____________________
Yamaha FZS600 (Now gone to heaven) > CBR600F4i (SOLD) > '99 YZF-R1
 Back to top
View user's profile Send private message Send e-mail You must be logged in to rate posts

goto10
World Chat Champion



Joined: 16 Oct 2011
Karma :

PostPosted: 22:28 - 23 Dec 2014    Post subject: Reply with quote

I did this very thing earlier this year - I put armoured cable in directly from the consumer unit and created a radial to the shed - this feeds into the shed's own little consumer unit. I then have the internal shed lights and sockets running on their own MCBs/RCD
I also fitted a remote control/timer thing on the outside of the shed (feeding from the little consumer unit), which runs the garden lights and fountain on a timer/remote control:

https://www.homeeasy.eu/RemoteControl4GangOutdoorSocketKit/HE440%20v2/191/Product/896/
____________________
'12 NC700S & '12 CB600F Hornet [Stolen by some dickless twat] Suzuki GT500 shed
 Back to top
View user's profile Send private message You must be logged in to rate posts

smegballs
World Chat Champion



Joined: 28 Oct 2007
Karma :

PostPosted: 22:35 - 23 Dec 2014    Post subject: Reply with quote

Chuffin Nora wrote:
Erm.

Might one enquire as for what purpose this shed is intended?



Fritzl basement, but no incest just abducted hookers. It's surprisingly hard to get an planning for incest outside of cornwall.
 Back to top
View user's profile Send private message Send e-mail You must be logged in to rate posts

Chuffin Nora
World Chat Champion



Joined: 02 Sep 2013
Karma :

PostPosted: 04:46 - 24 Dec 2014    Post subject: Reply with quote

smegballs wrote:
Chuffin Nora wrote:
Erm.

Might one enquire as for what purpose this shed is intended?



Fritzl basement, but no incest just abducted hookers. It's surprisingly hard to get an planning for incest outside of cornwall.

Er…
Well, after a quite unpleasant spell ruminating on the possibility of your being some private dick on to my dirty little secret, I finally got around to actually detecting the pertinent sentence:

weasley wrote:
The shed will mostly be storage, maybe a little workshop bench. It will never be used for heavy-duty stuff (I can do anything like this in the garage, should I ever need to).


Bang to rights!
____________________
There's a fine line between integrity
 Back to top
View user's profile Send private message You must be logged in to rate posts

Ribenapigeon
Super Spammer



Joined: 20 Feb 2012
Karma :

PostPosted: 08:19 - 24 Dec 2014    Post subject: Reply with quote

HT wrote:
My one tip.
Get a bigger shed. Girth is where it's at with sheds.


I second that. Whatever size you think will be good add at least fifty percent.
 Back to top
View user's profile Send private message You must be logged in to rate posts

Ribenapigeon
Super Spammer



Joined: 20 Feb 2012
Karma :

PostPosted: 08:27 - 24 Dec 2014    Post subject: Reply with quote

weasley wrote:
Thanks all. So conduit over armoured cable? I like the idea, as it is something I can do easily and then just get a spark in for one day to do the sparky bits.

Conduit; is that ribbed bendy pipe stuff a good idea, or are we talking PVC pipework?


There are sparky sites with forums. There's also a rules regs book you can get. I've lost mine but its not expensive. If your burying cable it has to be to certain depth and marked.
 Back to top
View user's profile Send private message You must be logged in to rate posts

Ribenapigeon
Super Spammer



Joined: 20 Feb 2012
Karma :

PostPosted: 08:36 - 24 Dec 2014    Post subject: Reply with quote

Furrybiker wrote:
Hate to hijack this but can I just ask a quick question?

I have a shed that I would like to power from the supply to the garage. It is only for a 150 watt security lamp and is about 15 metres from the garage.

Could I not just run an armoured cable from the RCD protected supply in the garage to the shed?

Or does this put me in breach of the regs?


I wanted to fix a security light on the side of my building. I asked a sparky and he said fused switched spur from socket ring is within regs.
 Back to top
View user's profile Send private message You must be logged in to rate posts

ScaredyCat
World Chat Champion



Joined: 19 May 2012
Karma :

PostPosted: 10:23 - 24 Dec 2014    Post subject: Reply with quote

This stuff is perfectly legal and doesn't require an electrician to wire it up. If you're only using it for lights it's going to be fine.
____________________
Honda CBF125 ➝ NC700X
Honda CBF125 ↳ Speed Triple
 Back to top
View user's profile Send private message You must be logged in to rate posts
Old Thread Alert!

The last post was made 11 years, 6 days ago. Instead of replying here, would creating a new thread be more useful?
  Display posts from previous:   
This page may contain affiliate links, which means we may earn a small commission if a visitor clicks through and makes a purchase. By clicking on an affiliate link, you accept that third-party cookies will be set.

Post new topic   Reply to topic    Bike Chat Forums Index -> Random Banter All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You cannot download files in this forum

Read the Terms of Use! - Powered by phpBB © phpBB Group
 

Debug Mode: ON - Server: birks (www) - Page Generation Time: 0.13 Sec - Server Load: 0.96 - MySQL Queries: 13 - Page Size: 131.84 Kb