 Posted: 12:09 - 04 Oct 2015 Post subject: How much to replace a conventional boiler with a combi? |
 |
|
Hi All,
Obviously the first place to go for plumbing advice is here on good ole' BCF so here it goes.
So, current boiler is probably as old as the house (around 16/17 years) and is an "Ideal NF40". It currently makes all manner of noises and is probably about as efficient as Concord...
The whole system looks to have been manipulated over the years but currently the set-up is a thermostat in the front room and then a tank in a cupboard in the bathroom with a danfoss control unit controlling a 3 port valve for either water, central heating or both. Oh, and it has a circulation pump (which I had to replace 2 years ago, grr).
As you can see, quite the monstrosity:
https://i258.photobucket.com/albums/hh258/JoeSnowden/20151004_120513_zps1bv7qusn.jpg
What I want is to get rid of the whole set up that's in the bathroom so we can get rid of the cupboard and just have a combi boiler in the kitchen and then a control unit in the front room where the thermostat is. The house is a reasonably sized 3 bed semi with only 8 radiators throughout. It's probably worth mentioning that water pressure isn't great and I like a decent shower (there's also a shower pump in the mix which gives a good (but loud!) shower and does a good job of emptying the hot water tank in no time at all...)
Firstly, I have no idea about rough costs as a starting point and all that I've seen seems to vary wildly in cost.
What sort of set up would I need to be able to heat up the house in a reasonable amount of time and provide water for the shower at decent pressure and sort of costs would I be looking at to remove the existing system (hot water tank and associated plumbing), supply and install the new one?
Any advice from either plumbers or those who have had similar work carried out would be much appreciated.
Thanks,
Joe ____________________ Current Bikes 650 Honda Bros, VTR1000 Firestorm // Past Bikes: Sachs Madass 50/110cc - Bandit 400 - FZR750
(+ a XS650 in lots of pieces in my garage and other places...) |
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| Keir |
This post is not being displayed .
|
 Keir World Chat Champion
Joined: 11 Apr 2006 Karma :   
|
 Posted: 12:21 - 04 Oct 2015 Post subject: |
 |
|
when I refurbished my house it had a very basic heating system installed with a tank like yours. similar house, 3 bed, 7 rads.
I ripped it all out and started from scratch with a plumber installing all new pipework, rads and combi. it cost £3200.
The shower now comes straight off the combi so it never runs out and shower pressure is fine, not quite pump pressure but much better than an electric shower. ____________________ Current : '08 Yamaha FZ1s
Previous: '99 Honda CBR 600FX, 03 ZX636 B1H, 99 Fazer 600 (red), 02 GSX-R 600 K2, 00 SV650s (red), 2008 ZX10R, 97 Bandit 1200N, 04 ZX6RR K1H, 04 GSX-R 1000, 98 Fazer 600 (gold), 05 Madness 110 Pit bike, 04 CR125R, 00 SV650s (black), 06 KTM 625 SMC, 99 SRAD 600 track bike, 03 SV650, 98 Bandit 1200N, Bandit 600SY, 03 GSX-R 600 K3, 01 GSX-R 600, 01 Fazer 600 (black), VFR 400 NC30 x3, 78 Honda Dream, 00 Speedfight 50 |
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| Polarbear |
This post is not being displayed .
|
 Polarbear Super Spammer

Joined: 24 Feb 2007 Karma :  
|
 Posted: 12:25 - 04 Oct 2015 Post subject: |
 |
|
I had the same system as you, immersion heater and crappy central heating boiler. I had it completely ripped out, new all singing and dancing combi boiler, pipework, rads etc. Five grand for everything done, even the sweeping up after.  ____________________ Victory Cross Country American tractor. |
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| Andy_Pagin |
This post is not being displayed .
|
 Andy_Pagin World Chat Champion

Joined: 08 Nov 2010 Karma :    
|
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| arry |
This post is not being displayed .
|
 arry Super Spammer
Joined: 03 Jan 2009 Karma :    
|
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| stinkwheel |
This post is not being displayed .
|
 stinkwheel Bovine Proctologist

Joined: 12 Jul 2004 Karma :    
|
 Posted: 13:58 - 04 Oct 2015 Post subject: |
 |
|
Combi boilers are unreliable pices of shit which render your heating system incapable of utilising any of the developing eco energy systems, all of which rely on having a heat store of some sort.
Think carefully before fitting one.
I want to fit solar heating an and a solar powered, ground-source heat pump but to do so would mean re-doing all the plumbing to fit a heat store again as well as installing a new, even more expensive combi that can cope with being fed pre-heated water.
I've had the engineer out to my combi boiler at least six times in the four years I've lived in this house. That's not counting the countless hours I've spent tracking down and fixing faults myself when I realised boiler engineers have no diagnostic skills whatsoever and simply replace bits (charged to you) until it starts working again. They have a certificate qualifying them as a boiler engineer but that just means they know how to fit parts safely without risking an explosion, it doesn't mean they actually know how to fix one.
Also remember that hot water tank is made of enough copper to be worth driving it down to the scrappy and cashing it in when they ask if you "like us to get rid if this for you" as if they're doing you a favour. ____________________ “Rule one: Always stick around for one more drink. That's when things happen. That's when you find out everything you want to know.”
I did the 2010 Round Britain Rally on my 350 Bullet. 89 landmarks, 3 months, 9,500 miles. |
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| J4mes |
This post is not being displayed .
|
 J4mes World Chat Champion
Joined: 18 Mar 2011 Karma :  
|
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| MCN |
This post is not being displayed .
|
 MCN Super Spammer

Joined: 22 Jul 2015 Karma :   
|
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| Andy_Pagin |
This post is not being displayed .
|
 Andy_Pagin World Chat Champion

Joined: 08 Nov 2010 Karma :    
|
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| sickpup |
This post is not being displayed .
|
 sickpup Old Timer

Joined: 21 Apr 2004 Karma :     
|
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| Polarbear |
This post is not being displayed .
|
 Polarbear Super Spammer

Joined: 24 Feb 2007 Karma :  
|
 Posted: 15:37 - 04 Oct 2015 Post subject: |
 |
|
My combi has been fine. It would be cause I have British Gas home care for my house.
Of course if I cancelled it the damn thing would break down a day later.  ____________________ Victory Cross Country American tractor. |
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| Andy_Pagin |
This post is not being displayed .
|
 Andy_Pagin World Chat Champion

Joined: 08 Nov 2010 Karma :    
|
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| Nobby the Bastard |
This post is not being displayed .
|
 Nobby the Bastard Harley Gaydar

Joined: 16 Aug 2013 Karma :  
|
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| MCN |
This post is not being displayed .
|
 MCN Super Spammer

Joined: 22 Jul 2015 Karma :   
|
 Posted: 17:50 - 04 Oct 2015 Post subject: |
 |
|
Your plumber should have plumbed in the pump to blend hot with cold water.
It saves tonnes of hot water and means that tank could easily make 4-5 decent 7-10 min showers.
Noisy boiler is normally air or a kack build up in the boiler tubes.
Normally due to none or insufficient inhibitor in the system.
If you can light the air that comes out the bleeders then there is no inhibitor. The gas produced is Rotten Egg Gas/H2S.
Scale can block the boiler too. and make all those crinking noises as it heats up.
You can flush the system with fresh water.
I use Fernox
Determine if you have an open system with a little top up tank or a closed system with a sealed accumulator/pressure tank. (If the later you need a filling loop if there is not one there. Buy a short hose from B&Q for that.)
Drain the system off.
Add a cleaner or de-scaler if required.
Flush again with fresh three or four times.
Add inhibitor and Boiler Silencer then
Fill with fresh water.
Bleeding as required.
If the boiler otherwise runs OK then it may save you a bob or two or even let you put a few quid away in a New Boiler account so it's not so painful.
It is quite a big purchase and there are deals for so much per month giving you 'piece of mind'.
As said my boiler is over ten years old and has cost me £150 to fit a new fan in that time. But I treat the system myself. ____________________ Disclaimer: The comments above may be predicted text and not necessarily the opinion of MCN. |
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| arry |
This post is not being displayed .
|
 arry Super Spammer
Joined: 03 Jan 2009 Karma :    
|
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| stinkwheel |
This post is not being displayed .
|
 stinkwheel Bovine Proctologist

Joined: 12 Jul 2004 Karma :    
|
 Posted: 20:46 - 04 Oct 2015 Post subject: |
 |
|
Last two "PCB's gone" in my boiler turned out to be an ineptly fitted flow switch. So £100 each plus labour as compared to rotating the flow switch so the arrow pointed in the direction of flow and not off on the piss.
Took me two hours, having never worked on one before, with a wiring diagram to come up with a diagnostic algorithm for the fault. Five minutes to remove the front panel to get at the (numbered) terrminal blocks. Approximately 5 minutes with a voltmeter to find the faulty componant, 10 minutes with screwdriver to get to the switch and five seconds to rotate it 30 degrees so it clicked every time instead of just some of the time.
Less time in total than it takes either of two "qualified" boiler engineers to diagnose and fit a PCB that didn't need changing.
There is of course an unnamed third party, neither of the two "engineers" who attended (or not that they are admitting to) who fitted the switch on the piss in the first place. ____________________ “Rule one: Always stick around for one more drink. That's when things happen. That's when you find out everything you want to know.”
I did the 2010 Round Britain Rally on my 350 Bullet. 89 landmarks, 3 months, 9,500 miles. |
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| arry |
This post is not being displayed .
|
 arry Super Spammer
Joined: 03 Jan 2009 Karma :    
|
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| Robby |
This post is not being displayed .
|
 Robby Dirty Old Man

Joined: 16 May 2002 Karma :   
|
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| 400bandit |
This post is not being displayed .
|
 400bandit World Chat Champion

Joined: 21 Dec 2005 Karma :  
|
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| Ste |
This post is not being displayed .
|
 Ste Not Work Safe

Joined: 01 Sep 2002 Karma :    
|
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| MCN |
This post is not being displayed .
|
 MCN Super Spammer

Joined: 22 Jul 2015 Karma :   
|
 Posted: 00:53 - 05 Oct 2015 Post subject: |
 |
|
Get to B&Q ASAP and buy yourself a boiler blanket. Wrap it around your boiler. You're probably are aware it's toastie warm in there. That's all your s heating up the sky.
Boiler blankets pay for them self in a couple of years and the psychological effect alone that your not paying a Spanish Money Magnate several pounds a year to buy his power is a comfort on it's own.
(There is a little bit of this heat adds to the 'overall heat' in the house which would/will be topped up by the heating system but the constant waste is the dog.)
Turn your tank thermostat down to about 60ºC. Cold is dangerous as you can encourage bad bacteria in cooler temps (legionella).
Buy and fit radiator reflector material on the wall behind radiators on all external walls ____________________ Disclaimer: The comments above may be predicted text and not necessarily the opinion of MCN. |
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| Tracey Suntan-King |
This post is not being displayed .
|
 Tracey Suntan-King World Chat Champion

Joined: 10 Nov 2012 Karma :   
|
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| grr666 |
This post is not being displayed .
|
 grr666 Super Spammer

Joined: 16 Jun 2014 Karma :   
|
 Posted: 11:24 - 05 Oct 2015 Post subject: |
 |
|
I think MCN means cylinder blanket.
My combi is fitted in my loft, it doesn't get in anybodies way there.
Had a Bosch Worcester fitted after having
the rubbish BAXI fireplace and back boiler setup removed. ____________________ Currently enjoying products from Ford, Mazda and Yamaha
Ste wrote: Avatars are fine, it's signatures that need turning off.  |
|
| Back to top |
|
You must be logged in to rate posts |
|
 |
| Cyclingbiker |
This post is not being displayed .
|
 Cyclingbiker Spanner Monkey

Joined: 05 Aug 2012 Karma :  
|
|