| A100man |
 A100man World Chat Champion
 Posted: 17:24 - 23 Mar 2021 Post subject: Electrical Test Fail in Flat - confused. |
A flat I have an interested in (part owned with ex-wife) failed an electrical test due to cooker supply incompatibity with CPC cable size. 6mm cable with 2.5mm CPC/Earth and a 30 A fuse/MCB.
Here's what he wrote..
'Coordination between conductors and overload protective devices (433.1; 533.2.1). is in
a dangerous condition and presents risk of injury. Immediate remedial action is required. Oven supply is undersized
2.5mm instead of 6mm earth cable on a 30amp fuse cut off so no fault protection'
Is this right? Do I have to installed an auxiliary earth?
BTW I'm having the CU changed to metal type with RCD . ____________________ Now: A100, SRX250, XJ598, FZ750, SL1000
Then: Fizz, RS200, KL250, XJ550, Laverda Alpina, XJ600, FZS600, Skorpion, GT 250 |
| Nobby the Bastard |
| A100man |
 Posted: 17:40 - 23 Mar 2021 Post subject: |
| Nobby the Bastard wrote: | It means the wire will melt before the circuit breaker will trip. |
BUT 2.5mm earth is standard for a 6mm T&E cable as far as I know. Most of the cookers and showers in the country must be connected using it. Or have I missed something.
I expect RCD protection will sort it - it usually does. ____________________ Now: A100, SRX250, XJ598, FZ750, SL1000
| Freddyfruitba... |
 Freddyfruitba... World Chat Champion
| Nobby the Bastard |
| Freddyfruitba... |
| Islander |
 Islander World Chat Champion
| MCN |
 MCN Super Spammer
 Posted: 18:30 - 23 Mar 2021 Post subject: |
Call a local electrician for estimates.
It won't be massively expensive and he'll not tale too long to run a heavier cable.
If it's an old house then a lot of cables will be easy to pull through with the new cable tied to it.
Failing that, then plaster and any capping over the cables may need to be removed and made good after. With some re-decoration involved too.
But with electrics it far better safer than sorrier.
I'd go for the bigger cable rather than a small breaker.
Some prick may replace the breaker for a bigger one and set fire to the place in the process.
Some community responsibility is advised.  ____________________ Disclaimer: The comments above may be predicted text and not necessarily the opinion of MCN. |
| A100man |
 Posted: 18:48 - 23 Mar 2021 Post subject: |
| Islander wrote: | Yep as others have said the fault is the cross sectional area (CSA) of the conductors rather than the cpc. It appears that 2.5mm2 has been installed instead of 6mm2.
6mm2 T&E carries a 2.5mm2 CPC which is perfectly fine. |
Yes this is that cable used. mention of 2.5mm is confusing as that is standard ring main stuff but int his case refers to the CPC - circuit protect conductor (aka Earth).
This is why I don't understand the report! ____________________ Now: A100, SRX250, XJ598, FZ750, SL1000
| A100man |
 Posted: 18:52 - 23 Mar 2021 Post subject: |
My only thought was that modern regs might not think 30A down a 2.5mm2 earth will trip fast enough - hence an RCD protection (or bigger earth) is needed ____________________ Now: A100, SRX250, XJ598, FZ750, SL1000
| A100man |
 Posted: 19:00 - 23 Mar 2021 Post subject: |
| MCN wrote: | Call a local electrician for estimates.
Ah well theres a thing. The rental agent got a quote for the works - 750 quid (plus VAT) for a 3 circuit CU swap! I got another electrician onto it but were trying to understand this part.. Is it a mistake? ____________________ Now: A100, SRX250, XJ598, FZ750, SL1000
| Freddyfruitba... |
| drzsta |
 drzsta World Chat Champion
| A100man |
 Posted: 20:15 - 23 Mar 2021 Post subject: |
| Freddyfruitbat wrote: | | A100man wrote: | Yes this is that cable used. mention of 2.5mm is confusing as that is standard ring main stuff but int his case refers to the CPC - circuit protect conductor (aka Earth).
This is why I don't understand the report! |
You and me both. I thought the wording on the report was your bit in italics, which doesn't mention "CPC" at all?
So do you actually know what size cable is fitted on the cooker circuit?
I was beginning to wonder but later in the report it definitely states it's 6mm2 conductors with 2.5mm2 earth/CPC. I'll be able to check on Saturday when I go in with my electrician mate... As it goes it's only powering a basic oven (gas hob) so we'll be able to sort it.. I just wondered if I'd missed some new 'cooker must have 6mm CPC' reg. ____________________ Now: A100, SRX250, XJ598, FZ750, SL1000
| steve the grease |
 steve the grease Crazy Courier
 Posted: 22:15 - 23 Mar 2021 Post subject: |
Seems clear to me that a 6mm twin and earth cable is made with a2.5mm earth cable. So The bloke doesn't know what the fuck he is talking about.
https://www.voltimum.co.uk/articles/q-day-cpc-sizes-twin-earth-cable-there-1 ____________________ All the above is my personal opinion, you can see my lips move, but I'm talking out of my arse.
I've been riding, and fixing , bikes for 50 years, in that time the more I learn, the less I am absolutely sure of..... |
| Islander |
| steve the grease |
The last post was made 5 years, 182 days ago. Instead of replying here, would creating a new thread be more useful? |